NFPA 72 6.8.5 addresses fire alarm system inputs where fire alarm systems are 
required.

Also 

5.15.3.3 A supervisory signal-initiating device for other than
pressure tanks shall initiate a low-water level signal when the
water level falls 300 mm (12 in.).
5.15.4 Water Temperature Supervisory Signal-Initiating Device.
A temperature supervisory device for a water storage container
exposed to freezing conditions shall initiate two separate and
distinctive signals. One signal shall indicate a decrease in water
temperature to 4.4°C (40°F) and the other shall indicate its
restoration to above 4.4°C (40°F).


NFPA 22, 2003
13.8* Sensors.
13.8.1 Provisions shall be made for the installation of sensors
in accordance with NFPA72®, National Fire Alarm Code®, for two
critical water temperatures and two critical water levels.

A.13.8 It is not the intent of this standard to require the electronic
supervision of tanks; however, where such supervision is
required in accordance with NFPA 72®, National Fire Alarm
Code®, the following alarms should be required:
(1) Water temperature below 4.4°C (40°F)
(2) Return of water temperature to 4.4°C 40°F
(3) Water level 76.2 mm (3 in.) (pressure tanks) or 127 mm
(5 in.) (all other tanks) below normal
(4) Return of water level to normal
(5) Pressure in pressure tank 0.48 kPa (10 psi) below normal
(6) Pressure in pressure tank 0.48 kPa (10 psi) above normal 


For your review..................

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Thursday, September 24, 2009 11:40 AM
To: [email protected]
Subject: Tank water alarms

Having trouble finding the required alarm points and water levels for tank 
water supplies.  Is monitoring of tank level even required?  I have 10% low 
water alarm in my head but can't source it.  Is it a rule of thumb?  Is it 10% 
below tank capacity or 10% below minimal required amount of water?  Many tanks 
are actually a bit bigger than theoretically necessary.  Unless I'm
missing it in NFPA 22 it appears only a gauge is required.   I know auto
refill is not required.  NFPA 25 doesn't help, it clearly suggests some tanks 
have monitoring thus a quarterly insp. some don't and a monthly.  So if it's 
just a gauge we are apparently relying on someone actually looking at it and 
getting it refilled sometime before the fire starts hopefully?  

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [email protected]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to