NFPA 72 (07) section 5.13.3 describes two supervisory signals shall be
initiated.   One for low/high level and one indicating restoring to normal
level.  Doesn't say 10% or otherwise.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213

[email protected] wrote on 09/24/2009 10:39:51 AM:

> [image removed]
>
> Tank water alarms
>
> Chris Cahill
>
> to:
>
> sprinklerforum
>
> 09/24/2009 10:39 AM
>
> Sent by:
>
> [email protected]
>
> Please respond to sprinklerforum
>
> Having trouble finding the required alarm points and water levels for
tank
> water supplies.  Is monitoring of tank level even required?  I have 10%
low
> water alarm in my head but can't source it.  Is it a rule of thumb?  Is
it
> 10% below tank capacity or 10% below minimal required amount of water?
Many
> tanks are actually a bit bigger than theoretically necessary.  Unless I'm
> missing it in NFPA 22 it appears only a gauge is required.   I know auto
> refill is not required.  NFPA 25 doesn't help, it clearly suggests some
> tanks have monitoring thus a quarterly insp. some don't and a monthly.
So
> if it's just a gauge we are apparently relying on someone actually
looking
> at it and getting it refilled sometime before the fire starts hopefully?

>
>
>
> Chris Cahill, P.E.
>
> Fire Protection Engineer
>
> Sentry Fire Protection, Inc.
>
>
>
> 763-658-4483
>
> 763-658-4921 fax
>
>
>
> Email: [email protected]
>
>
>
> Mail: P.O. Box 69
>
>         Waverly, MN 55390
>
>
>
> Location: 4439 Hwy 12 SW
>
>               Waverly, MN 55390
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to