Mark,

Like Steve said, the requirement comes from the UFC codes - section and
verse below

2-3.1.1.1 Hydraulic calculations must include a minimum pressure drop across
backflow preventers of 12 psi (82.7 kPa), or the actual pressure drop,
whichever is greater, regardless of type or size.

What really gets me about this is that I think this is because they are
afraid that eventually an RPZ will be put in and they want to design for
that, but even some of the new RPZ's now can be designed for less than 12
psi and many times increase can put you into a fire pump.  Also, once a
double-check is deemed acceptable as the BFP, very little is likely to
change that would require adding an RPZ - short of adding an antifreeze loop
or something.

I'm with you on the 3,000 sqft design area.  It makes no sense to me.  I
could see increasing the density, because suppression is all about delivery
rate, but doubling the design area just adds a lot of unnecessary water in
my opinion.  

Any government folks know where those requirements originate from?


Steve Kowkabany, P.E.
Fire Protection Engineer
Neptune Fire Protection Engineering LLC
616 Davis Street
Neptune Beach, FL 32266
904-652-4200 Phone
904-212-0868 Fax 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mark Sornsin
Sent: Thursday, September 24, 2009 10:12 AM
To: '[email protected]'
Subject: RE: Inadequte Water

Steve:

Which UFL standard is requiring the 12 psi drop across the backflow?  This
is the second time I've heard of this but have not yet had to deal with it
(I don't know why not).

I would LOVE to have a sit-down with the 'powers that be' responsible for
the UFC standards. E.g. where do they get the 3,000 sq.ft design area crap?
They say it's common HPR requirements in the civilian world - except I
worked for FM and we NEVER required 3,000 sq.ft. design areas for light or
ordinary hazard-equivalent occupancies. Maybe they just want to cover
themselves in case a combustible concealed space appears...

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104-7079

Direct:    701. 280.8591
Fax:        701.280.8739
Cell:        701.371.5759

[email protected]
www.ulteig.com

Confidentiality Notice
This message may contain privileged and confidential information. If you
think, for any reason, this message may have been addressed to you in error,
you   must not disseminate copy or take any action in reliance on it, and we
would ask you to notify me immediately by return email to
[email protected].



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Kowkabany
Sent: Thursday, September 24, 2009 7:18 AM
To: [email protected]
Subject: RE: Inadequte Water

I have the single most frustrating water issue I have ever had going on
right now Greg.  I am working on this small commercial entrance facility at
a military base in Georgia.  We are only sprinklering a small 3,800 sqft
cargo transfer building and getting the water from the local utility rather
than the base.

We designed based on modeling data that was the only thing available at
design (there was no water within a mile then) and had no problem making the
small light hazard wet system work.

Last week the underground was finally finished and we had our main run up to
the building and some nearby hydrants to test, so we tested them - 55/25 at
750 gpm.  Bad water but still enough to make an little light hazard wet
system work right?

Not once you take a 3,000 sqft design area, a 500 gpm hose allowance due to
the presence of 300 sqft of OH1 rooms, and a mandatory 12 psi pressure
across the BFP regardless of the fact that it is actually a double-check -
all mandatory per UFC codes.  After all that, you need 850 gpm at 40 psi to
make this system work and we are looking at a pump and a tank!

It's a very frustrating situation, so feel free to tell your AHJ he is not
alone.


Steve Kowkabany, P.E.
Fire Protection Engineer
Neptune Fire Protection Engineering LLC
616 Davis Street
Neptune Beach, FL 32266
904-652-4200 Phone
904-212-0868 Fax

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
No virus found in this incoming message.
Checked by AVG - www.avg.com 
Version: 8.5.409 / Virus Database: 270.13.111/2386 - Release Date: 09/24/09
05:52:00

_______________________________________________