Steve,

Is this requirement also in a spec, or are you basing this requirement
solely on the section of the draft copy of 3-600-10N?

If its the latter, I don't believe that a draft copy of a new UFC series is
in enforceable.  I stopped doing government work two months ago, so unless
something has changed since then, the only thing you have to worry about is
3-600-01 and the project's UFGS spec.

If someone from the corps is referencing this standard, I think you may want
to ask why they're using a draft document.

-Ben

On Thu, Sep 24, 2009 at 3:17 PM, Steve Kowkabany <[email protected]>wrote:

> Mark,
>
> Like Steve said, the requirement comes from the UFC codes - section and
> verse below
>
> 2-3.1.1.1 Hydraulic calculations must include a minimum pressure drop
> across
> backflow preventers of 12 psi (82.7 kPa), or the actual pressure drop,
> whichever is greater, regardless of type or size.
>
> What really gets me about this is that I think this is because they are
> afraid that eventually an RPZ will be put in and they want to design for
> that, but even some of the new RPZ's now can be designed for less than 12
> psi and many times increase can put you into a fire pump.  Also, once a
> double-check is deemed acceptable as the BFP, very little is likely to
> change that would require adding an RPZ - short of adding an antifreeze
> loop
> or something.
>
> I'm with you on the 3,000 sqft design area.  It makes no sense to me.  I
> could see increasing the density, because suppression is all about delivery
> rate, but doubling the design area just adds a lot of unnecessary water in
> my opinion.
>
> Any government folks know where those requirements originate from?
>
>
> Steve Kowkabany, P.E.
> Fire Protection Engineer
> Neptune Fire Protection Engineering LLC
> 616 Davis Street
> Neptune Beach, FL 32266
> 904-652-4200 Phone
> 904-212-0868 Fax
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Mark
> Sornsin
> Sent: Thursday, September 24, 2009 10:12 AM
> To: '[email protected]'
> Subject: RE: Inadequte Water
>
> Steve:
>
> Which UFL standard is requiring the 12 psi drop across the backflow?  This
> is the second time I've heard of this but have not yet had to deal with it
> (I don't know why not).
>
> I would LOVE to have a sit-down with the 'powers that be' responsible for
> the UFC standards. E.g. where do they get the 3,000 sq.ft design area crap?
> They say it's common HPR requirements in the civilian world - except I
> worked for FM and we NEVER required 3,000 sq.ft. design areas for light or
> ordinary hazard-equivalent occupancies. Maybe they just want to cover
> themselves in case a combustible concealed space appears...
>
> Mark A. Sornsin, PE
> Fire Protection Engineer
> Ulteig Engineers, Inc.
> 3350 38th Avenue S.
> Fargo, ND 58104-7079
>
> Direct:    701. 280.8591
> Fax:        701.280.8739
> Cell:        701.371.5759
>
> [email protected]
> www.ulteig.com
>
> Confidentiality Notice
> This message may contain privileged and confidential information. If you
> think, for any reason, this message may have been addressed to you in
> error,
> you   must not disseminate copy or take any action in reliance on it, and
> we
> would ask you to notify me immediately by return email to
> [email protected].
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve
> Kowkabany
> Sent: Thursday, September 24, 2009 7:18 AM
> To: [email protected]
> Subject: RE: Inadequte Water
>
> I have the single most frustrating water issue I have ever had going on
> right now Greg.  I am working on this small commercial entrance facility at
> a military base in Georgia.  We are only sprinklering a small 3,800 sqft
> cargo transfer building and getting the water from the local utility rather
> than the base.
>
> We designed based on modeling data that was the only thing available at
> design (there was no water within a mile then) and had no problem making
> the
> small light hazard wet system work.
>
> Last week the underground was finally finished and we had our main run up
> to
> the building and some nearby hydrants to test, so we tested them - 55/25 at
> 750 gpm.  Bad water but still enough to make an little light hazard wet
> system work right?
>
> Not once you take a 3,000 sqft design area, a 500 gpm hose allowance due to
> the presence of 300 sqft of OH1 rooms, and a mandatory 12 psi pressure
> across the BFP regardless of the fact that it is actually a double-check -
> all mandatory per UFC codes.  After all that, you need 850 gpm at 40 psi to
> make this system work and we are looking at a pump and a tank!
>
> It's a very frustrating situation, so feel free to tell your AHJ he is not
> alone.
>
>
> Steve Kowkabany, P.E.
> Fire Protection Engineer
> Neptune Fire Protection Engineering LLC
> 616 Davis Street
> Neptune Beach, FL 32266
> 904-652-4200 Phone
> 904-212-0868 Fax
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> No virus found in this incoming message.
> Checked by AVG - www.avg.com
> Version: 8.5.409 / Virus Database: 270.13.111/2386 - Release Date: 09/24/09
> 05:52:00
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to