I got shot down in a high-rise on this; but there is an exception in IBC for the playing surfaces in indoor arenas or similar things that may help- But from an FPE point of view, there's no cooling of steel without the spkrs throughout; just because there's no fire load doesn't mean the heat won't follow the slope up over the pool and affect its integrity.
glc -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brown, Mike Sent: Thursday, October 22, 2009 8:51 AM To: [email protected] Subject: Protection over indoor swimming pools? Can someone point us in the right direction... we are being directed not to sprinkler over top the pools at an aquatic center they are only asking for the floor area around the pools? Has anyone had any experience with this situation? We can't find anything in nfpa? Mike Brown Project Designer Sunland Fire Protection 1218 Elon Place High Point, NC 27263 Ph. 336.886.7027 Ext. 140 Fax: 336.886.7024 WWW.SUNLANDFIRE.COM <http://WWW.SUNLANDFIRE.COM> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)