Pool areas without spectator seating is A-3 occupancy per IBC.

A-3 Assembly uses intended for worship, recreation or
amusement and other assembly uses not classified elsewhere
in Group A including, but not limited to:
-Indoor swimming pools (without spectator seating)

[F] 903.2.1 Group A. An automatic sprinkler system shall
be provided throughout buildings and portions thereof used
as Group A occupancies as provided in this section. For
Group A-1, A-2, A-3 and A-4 occupancies, the automatic
sprinkler system shall be provided throughout the floor area
where the Group A-1, A-2, A-3 or A-4 occupancy is
located, and in all floors between the Group A occupancy
and the level of exit discharge. For Group A-5 occupancies,
the automatic sprinkler system shall be provided in the
spaces indicated in Section 903.2.1.5.

Specific to A-3:
[F] 903.2.1.3 Group A-3. An automatic sprinkler system
shall be provided for Group A-3 occupancies where
one of the following conditions exists:
1. The fire area exceeds 12,000 square feet (1115 m2).
2. The fire area has an occupant load of 300 or more.
3. The fire area is located on a floor other than the level of exit discharge.

Exception: Areas used exclusively as participant
sports areas where the main floor area is located at the
same level as the level of exit discharge of the main
entrance and exit.

-----------------------------------------------------------------------
So if you meet the requirement to provide sprinklers per 903.2.1.3 what do the 
terms "throughout" and "floor area" mean?  "throughout" means "in or to every 
part, everywhere" according to Merriam-Webster; Floor Area, does that refer to 
the actual hard walkable floor or the floor level of the building on which the 
sprinklers will be located?  Seems that it is the overall floor area of a level 
of a building, not just the hard floor as opposed to the water surface of a 
pool area.

If you're required to provide sprinklers throughout and you omit them over the 
pool then your spacings are not compliant.   If the room has a peaked roof line 
and the pool is beneath that, where will combustion products gather, over the 
pool.

Several things to consider but there is no specific wording allowing the 
omission of sprinklers over a pool in the building code.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brown, Mike
Sent: Thursday, October 22, 2009 8:51 AM
To: [email protected]
Subject: Protection over indoor swimming pools?

Can someone point us in the right direction... we are being directed not to 
sprinkler over top the pools at an aquatic center they are only asking for the 
floor area around the pools? Has anyone had any experience with this situation? 
We can't find anything in nfpa?

 

Mike Brown

Project Designer

Sunland Fire Protection

1218 Elon Place 

High Point, NC 27263

Ph. 336.886.7027 Ext. 140

Fax: 336.886.7024

WWW.SUNLANDFIRE.COM <http://WWW.SUNLANDFIRE.COM> 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to