Anyone come across fit-ups where short drops have been removed and replaced 
with 4' or 6' flexible piping to new head locations?  Original calcs account 
for 2' drop with two elbows, and 2 feet additional standard pipe and has a 
4psi reserve above available.  As-Builts give new head locations showing 
proper coverage, no new calcs provided.  Simple daywork job, 130 plus or 
minus relo's and flex drops sure make it easy!
I do not see where this condition would be covered in an Inspection for 
inclusion on a Report.  And some AHJs are not appreciative of 
"interference".
Suggestions?

Garth 