We have done some of fit ups utilizing flex drops as you say, but we know the impact they can have and how tight some calcs are. If we sway from the original we at least do proof calcs. If its small enough we don't have to provide calcs to the local AHJ for permitting and only need to supply a letter of intent, we mention the fact that the flex drops will be utilized and we have proof calcs if required.
Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Thursday, October 29, 2009 12:34 PM To: [email protected] Subject: Re: fit-up using flexible drop piping Did you notice this as part of an ITM contract? I would do separate a "while we were at this location" letter to the owner. There is some level of moral (and legal) responsibility to report something that could be a dangerous condition. Is the "interference" because the AHJ might have missed something? At 12:58 PM 10/29/2009, you wrote: >Anyone come across fit-ups where short drops have been removed and replaced >with 4' or 6' flexible piping to new head locations? Original calcs account >for 2' drop with two elbows, and 2 feet additional standard pipe and has a >4psi reserve above available. As-Builts give new head locations showing >proper coverage, no new calcs provided. Simple daywork job, 130 plus or >minus relo's and flex drops sure make it easy! >I do not see where this condition would be covered in an Inspection for >inclusion on a Report. And some AHJs are not appreciative of >"interference". >Suggestions? > >Garth > > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)