Did you notice this as part of an ITM contract? I would do separate a 
"while we were at this location" letter to the owner. There is some 
level of moral (and legal) responsibility to report something that 
could be a dangerous condition. Is the "interference" because the AHJ 
might have missed something?


At 12:58 PM 10/29/2009, you wrote:
>Anyone come across fit-ups where short drops have been removed and replaced
>with 4' or 6' flexible piping to new head locations?  Original calcs account
>for 2' drop with two elbows, and 2 feet additional standard pipe and has a
>4psi reserve above available.  As-Builts give new head locations showing
>proper coverage, no new calcs provided.  Simple daywork job, 130 plus or
>minus relo's and flex drops sure make it easy!
>I do not see where this condition would be covered in an Inspection for
>inclusion on a Report.  And some AHJs are not appreciative of
>"interference".
>Suggestions?
>
>Garth
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to