No takers??


--- On Fri, 10/30/09, Ralphy Henderson <[email protected]> wrote:

From: Ralphy Henderson <[email protected]>
Subject: Omitting sprinklers (13 - 22.4.4.6.2)
To: [email protected]
Date: Friday, October 30, 2009, 5:55 PM

NFPA #13 22.4.4.6.2. allows ommitting sprinklers from the calcs in certain 
circumstances with the understanding that those sprinklers ommitted will still 
need to be able to discharge at the minimum density. 

Does this mean that I can omit sprinklers in the calc then just make sure the 
armover and branchline sizes established by the calcs are maintained in sizing 
that particular sprinklers piping?  So if I establish pipe sizes as 1", 1", 1 
1/4", 1 1/2" to each sprinkler on the line I just make sure to not forget to 
include the head in the closet as part of the overall sizing scheme?

Or...????


Thanks,

RB



For reference:

22.4.4.6.2  The requirements of 22.4.4.6.1 to include every sprinkler in the 
design area to be included in the system discharge shall not apply where the 
area of application is equal to or greater than the minimum allowable area of 
Figure 11.2.3.1.1 for the appropriate hazard classification (including a 30 
percent increase for dry pipe systems). Sprinkler discharge in closets, 
washrooms, and similar small compartments requiring only one sprinkler shall be 
permitted to be omitted from hydraulic calculations within the area of 
application. Sprinklers in these small compartments shall, however, be capable 
of discharging minimum densities in accordance with Figure 11.2...3.1.1. 



      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to