1" to the drops should do you fine regardless of where it is in the
schedule.  Don't forget full 1500 sq.ft. calc.   

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ralphy
Henderson
Sent: Monday, November 02, 2009 12:20 PM
To: [email protected]
Subject: Re: Omitting sprinklers (13 - 22.4.4.6.2)

No takers??



--- On Fri, 10/30/09, Ralphy Henderson <[email protected]> wrote:

From: Ralphy Henderson <[email protected]>
Subject: Omitting sprinklers (13 - 22.4.4.6.2)
To: [email protected]
Date: Friday, October 30, 2009, 5:55 PM

NFPA #13 22.4.4.6.2. allows ommitting sprinklers from the calcs in certain
circumstances with the understanding that those sprinklers ommitted will
still need to be able to discharge at the minimum density. 

Does this mean that I can omit sprinklers in the calc then just make sure
the armover and branchline sizes established by the calcs are maintained in
sizing that particular sprinklers piping?  So if I establish pipe sizes as
1", 1", 1 1/4", 1 1/2" to each sprinkler on the line I just make sure to not
forget to include the head in the closet as part of the overall sizing
scheme?

Or...????


Thanks,

RB



For reference:

22.4.4.6.2  The requirements of 22.4.4.6.1 to include every sprinkler in the
design area to be included in the system discharge shall not apply where the
area of application is equal to or greater than the minimum allowable area
of Figure 11.2.3.1.1 for the appropriate hazard classification (including a
30 percent increase for dry pipe systems). Sprinkler discharge in closets,
washrooms, and similar small compartments requiring only one sprinkler shall
be permitted to be omitted from hydraulic calculations within the area of
application. Sprinklers in these small compartments shall, however, be
capable of discharging minimum densities in accordance with Figure
11.2...3.1.1. 



      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to