>--- On Fri, 10/30/09, Ralphy Henderson <[email protected]> wrote:
>
>From: Ralphy Henderson <[email protected]>
>Subject: Omitting sprinklers (13 - 22.4.4.6.2)
>To: [email protected]
>Date: Friday, October 30, 2009, 5:55 PM
>
>NFPA #13 22.4.4.6.2. allows ommitting sprinklers from the calcs in 
>certain circumstances with the understanding that those sprinklers 
>ommitted will still need to be able to discharge at the minimum density.
>
>Does this mean that I can omit sprinklers in the calc then just make 
>sure the armover and branchline sizes established by the calcs are 
>maintained in sizing that particular sprinklers piping?  So if I 
>establish pipe sizes as 1", 1", 1 1/4", 1 1/2" to each sprinkler on 
>the line I just make sure to not forget to include the head in the 
>closet as part of the overall sizing scheme?
>
>Or...????
>
>
>Thanks,
>
>RB
>
>
>
>For reference:
>
>22.4.4.6.2  The requirements of 22.4.4.6.1 to include every 
>sprinkler in the design area to be included in the system discharge 
>shall not apply where the area of application is equal to or greater 
>than the minimum allowable area of Figure 11.2.3.1.1 for the 
>appropriate hazard classification (including a 30 percent increase 
>for dry pipe systems). Sprinkler discharge in closets, washrooms, 
>and similar small compartments requiring only one sprinkler shall be 
>permitted to be omitted from hydraulic calculations within the area 
>of application. Sprinklers in these small compartments shall, 
>however, be capable of discharging minimum densities in accordance 
>with Figure 11.2...3.1.1.
>
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to