We have a flat roof canopy in front of a strip mall whose structure is non 
combustible, flat roof with bar joists 4-5' on center and a metal pan roof. The 
front of the canopy is a façade that is nearly vertical but slopes out at the 
bottom, probably a 4 FEET on 12 INCH slope. The framing for the façade is all 
2x4 with plywood and the ceiling of the canopy is all 2x4 with plywood - both 
of which are 2' on center. The height of this space varies due to the ceiling, 
but is approximately 7' tall.

According to table 8.6.2.2.1(a) I can space the heads at 225' with members over 
3' on center. Since the ROOF structure is non combustible, would I consider 
this my MEMBERS and use 225 sq ft, or do I have to use the ceiling framing as 
the MEMBERS and be limited to 130 sqft?

To be honest I would be great with 150 sq ft, but the 130 hurts the calcs due 
to the additional heads in the remote area.

Thanks for the input.

Greg McGahan
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum