On Nov 4, 2009, at 8:15 AM, Greg McGahan wrote:

> We have a flat roof canopy in front of a strip mall whose structure  
> is non combustible, flat roof with bar joists 4-5' on center and a  
> metal pan roof. The front of the canopy is a façade that is nearly  
> vertical but slopes out at the bottom, probably a 4 FEET on 12 INCH  
> slope. The framing for the façade is all 2x4 with plywood and the  
> ceiling of the canopy is all 2x4 with plywood - both of which are 2'  
> on center. The height of this space varies due to the ceiling, but  
> is approximately 7' tall.
>
> According to table 8.6.2.2.1(a) I can space the heads at 225' with  
> members over 3' on center. Since the ROOF structure is non  
> combustible, would I consider this my MEMBERS and use 225 sq ft, or  
> do I have to use the ceiling framing as the MEMBERS and be limited  
> to 130 sqft?
>
> To be honest I would be great with 150 sq ft, but the 130 hurts the  
> calcs due to the additional heads in the remote area.
>
> Thanks for the input.
>
> Greg McGahan
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to