Is the front of a strip mall LH? I'd think not. Hereabouts the
merchants put there most combustible seasonal stuff out front under
the canopy and create skinny little aisles on the sidewalks.

On Wed, Nov 4, 2009 at 8:15 AM, Greg McGahan <[email protected]> wrote:
> We have a flat roof canopy in front of a strip mall whose structure is non 
> combustible, flat roof with bar joists 4-5' on center and a metal pan roof. 
> The front of the canopy is a façade that is nearly vertical but slopes out at 
> the bottom, probably a 4 FEET on 12 INCH slope. The framing for the façade is 
> all 2x4 with plywood and the ceiling of the canopy is all 2x4 with plywood - 
> both of which are 2' on center. The height of this space varies due to the 
> ceiling, but is approximately 7' tall.
>
> According to table 8.6.2.2.1(a) I can space the heads at 225' with members 
> over 3' on center. Since the ROOF structure is non combustible, would I 
> consider this my MEMBERS and use 225 sq ft, or do I have to use the ceiling 
> framing as the MEMBERS and be limited to 130 sqft?
>
> To be honest I would be great with 150 sq ft, but the 130 hurts the calcs due 
> to the additional heads in the remote area.
>
> Thanks for the input.
>
> Greg McGahan
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to