The 2 questions below caused some discussion in my professional environment:

For Palletized, Solid Piled, Bin Boxes, or Shelf 
Storage NFPA 13 - 2007 paragraph 14.6 and 15.5, both tell us:

“High Expansion Foam — Reduction to Ceiling Density.
A reduction in ceiling density to one-half that 
required for Class I through Class IV 
commodities, idle pallets, or plastics shall be 
permitted without revising the design area, but 
the density shall be no less than 0.15 gpm/ft2 (6.1 mm/min).”

For Rack Storage of Class I Through Class IV 
Commodities Stored Over 25 ft (7.6 m) in Height paragraph 16.3.5.1 tells us:

“Where high-expansion foam systems are used for 
storage over 25 ft (7.6 m) high up to and 
including 35 ft (10.7 m) high, they shall be used 
in combination with ceiling sprinklers. The 
maximum submergence time for the high-expansion 
foam shall be 5 minutes for Class I, Class II, or 
Class III commodities and 4 minutes for Class IV commodities.”

Paragraph 12.12.2.2 tells us how to protect idle 
plastic pallets by the combination of hi-ex foam and sprinklers.

Nothing in section 12.12.1 about idle wooden pallets and hi-ex foam.
Questions:
- Can high stacks or rack storage of idle wooden 
pallets be protected by the combination of hi-ex foam and sprinklers?
- Can of idle wooden pallets be protected by hi-ex foam without sprinklers?

My opinion is that hi-ex foam only (without 
sprinklers) will not extinguish a fire in high 
stacks or rack storage of idle wooden pallets, 
because wooden pallets contain a lot of air by 
themselves and the foam will not penetrate inside 
the stacks. The foam will only envelop the 
complete stacks but will not prevent the air 
(oxygen) inside the stacks from reaching the wood.
Foam, however, may hinder the fire from jumping 
from one stack or rack to another, when sprinklers do their extinguishing job.

Please share your opinion.


Frans Stoop
TOS architecture & fire protection
Netherlands <[email protected]>
Tel. +31-24-324 0112  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to