There are many issues to consider when entertaining thoughts of using hi-ex 
foam.  Make sure it's the only valid choice before committing to using it.

The reason there is no mention of foam with wood pallets is because wood 
pallets are already addressed by 13 to be protected by water based sprinklers.  
Foam would not be appropriate or provide the same soaking that water would.

There are structural issues and ventilation issues to deal with when using 
hi-ex foam.  For a new install that might not be a big deal but for an existing 
building the cost impact can be rather significant.

Water based sprinklers ought to be first choice unless the commodity being 
protected can not be effectively protected by water and foam is recommended by 
either MSDS or NFPA or other resource. 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Frans Stoop
Sent: Monday, November 23, 2009 12:50 PM
To: [email protected]
Subject: Storage of idle wooden pallets and hi-ex foam

Dear colleagues,

The 2 questions below caused some discussion in my professional environment:

For Palletized, Solid Piled, Bin Boxes, or Shelf Storage NFPA 13 - 2007 
paragraph 14.6 and 15.5, both tell us:

"High Expansion Foam - Reduction to Ceiling Density.
A reduction in ceiling density to one-half that required for Class I through 
Class IV commodities, idle pallets, or plastics shall be permitted without 
revising the design area, but the density shall be no less than 0.15 gpm/ft2 
(6.1 mm/min)."

For Rack Storage of Class I Through Class IV Commodities Stored Over 25 ft (7.6 
m) in Height paragraph 16.3.5.1 tells us:

"Where high-expansion foam systems are used for storage over 25 ft (7.6 m) high 
up to and including 35 ft (10.7 m) high, they shall be used in combination with 
ceiling sprinklers. The maximum submergence time for the high-expansion foam 
shall be 5 minutes for Class I, Class II, or Class III commodities and 4 
minutes for Class IV commodities."

Paragraph 12.12.2.2 tells us how to protect idle plastic pallets by the 
combination of hi-ex foam and sprinklers.

Nothing in section 12.12.1 about idle wooden pallets and hi-ex foam.
Questions:
- Can high stacks or rack storage of idle wooden pallets be protected by the 
combination of hi-ex foam and sprinklers?
- Can of idle wooden pallets be protected by hi-ex foam without sprinklers?

My opinion is that hi-ex foam only (without
sprinklers) will not extinguish a fire in high stacks or rack storage of idle 
wooden pallets, because wooden pallets contain a lot of air by themselves and 
the foam will not penetrate inside the stacks. The foam will only envelop the 
complete stacks but will not prevent the air
(oxygen) inside the stacks from reaching the wood.
Foam, however, may hinder the fire from jumping from one stack or rack to 
another, when sprinklers do their extinguishing job.

Please share your opinion.


Frans Stoop
TOS architecture & fire protection
Netherlands <[email protected]>
Tel. +31-24-324 0112
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to