I've got a calc I'm reviewing, after all said and done, 3.63 psi margin between demand and available. Designer used 4.2K heads to get the flow exactly to the decimal of the required flow. This is an industrial type project. With a .15 gpm/sf density at 92 sf per head, the flow would be 13.8 gpm and he's dead on the money. The concern would be that over the years if there was any change in the water supply or decay of the piping, that the operation of half the design area would be questionable.
Would you approve or reject this design? Is this cutting it just a bit close? Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)