They already took the 10% off the available pressures so their actual margin 
would be around 10-11 psi without the 10% decrease,  but here's another twist,  
the test hydrant is not on the same water main that serves the site and is 
several hundred to a thousand feet away.  So there is some question as to the 
real value of the test in relation to what is actually available at the site.  
Calcs say test to riser is less than 10ft.  


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Monday, November 30, 2009 3:14 PM
To: [email protected]
Subject: RE: Calcs-How much margin

Did they observe a safety margin below the actual flow test result?   If
you take 10% off the available to start and still have 3.63 PSI, then sure.  
But if that's 3.63 PSI below the actual flow test result then unless the water 
supply is ... umm, distressed, it doesn't sound like a good idea.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, November 30, 2009 12:11 PM
To: [email protected]
Subject: Calcs-How much margin

I've got a calc I'm reviewing, after all said and done, 3.63 psi margin between 
demand and available.  Designer used 4.2K heads to get the flow exactly to the 
decimal of the required flow.  This is an industrial type project.  With a .15 
gpm/sf density at 92 sf per head, the flow would be
13.8 gpm and he's dead on the money.  The concern would be that over the years 
if there was any change in the water supply or decay of the piping, that the 
operation of half the design area would be questionable.  

Would you approve or reject this design?  Is this cutting it just a bit close?

 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 4650 (20091130) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 4650 (20091130) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to