I would approve it.
I would also check the calculations VERY, VERY close.

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
** Note new email address: [email protected]
 
-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, November 30, 2009 2:11 PM
To: [email protected]
Subject: Calcs-How much margin

I've got a calc I'm reviewing, after all said and done, 3.63 psi margin between 
demand and available.  Designer used 4.2K heads to get the flow exactly to the 
decimal of the required flow.  This is an industrial type project.  With a .15 
gpm/sf density at 92 sf per head, the flow would be 13.8 gpm and he's dead on 
the money.  The concern would be that over the years if there was any change in 
the water supply or decay of the piping, that the operation of half the design 
area would be questionable.  

Would you approve or reject this design?  Is this cutting it just a bit close?

 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to