Trouble is with as tight as this is, it's too late to fix things at that point 
in time. 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mike Hairfield
Sent: Monday, November 30, 2009 3:17 PM
To: AFSA SprinklerFORUM
Subject: RE: Calcs-How much margin


I would approve it but ask for "As Built" Calcs!!!!!

 

Mike
 
> From: [email protected]
> To: [email protected]
> Date: Mon, 30 Nov 2009 14:15:07 -0600
> Subject: RE: Calcs-How much margin
> 
> I would approve it.
> I would also check the calculations VERY, VERY close.
> 
> David Autry
> Plans Examiner
> Nebraska State Fire Marshal's Office
> 246 S. 14th Street
> Lincoln, NE 68508
> 402-471-9659
> 402-471-3118 fax
> www.sfm.ne.gov
> 
> ** Note new email address: [email protected]
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Monday, November 30, 2009 2:11 PM
> To: [email protected]
> Subject: Calcs-How much margin
> 
> I've got a calc I'm reviewing, after all said and done, 3.63 psi margin 
> between demand and available. Designer used 4.2K heads to get the flow 
> exactly to the decimal of the required flow. This is an industrial type 
> project. With a .15 gpm/sf density at 92 sf per head, the flow would be 13.8 
> gpm and he's dead on the money. The concern would be that over the years if 
> there was any change in the water supply or decay of the piping, that the 
> operation of half the design area would be questionable. 
> 
> Would you approve or reject this design? Is this cutting it just a bit close?
> 
> 
> 
> 
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 
> 864.599.8439 [email protected] http://www.ch2m.com
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to