This is one of those cases where in racing we used to say that if the rules 
don't say you can, assume you can't.

It would be harder to argue that the wording is permissive for use in OH when 
there's no direct text stating such and especially when the commentary takes a 
definitive position.

 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ed Kramer
Sent: Tuesday, December 01, 2009 9:58 AM
To: [email protected]
Subject: RE: Calcs-How much margin

Ron, I'm with you.  Nothing in 8.3.4.1 prohibits small orifice sprinks in OH.  
The commentary to section 8.3.4.1 then makes a leap of faith and says 
otherwise.  

There was a proposal in the 2010 ROP that would have changed 8.3.4.1.  The 
committee rejected it and said "The submitter is correct, this [using small 
orifice sprinks in OH hazard] is not allowed, it violates the listing of the 
sprinklers."  Yea, that helps.  Another proposal was submitted at the ROC level 
and was also rejected.

It seems to me the intent of 8.3.4.1 is to not allow small orifice sprinks in 
OH, but someone was on crack when they wrote it.

Ed Kramer
Littleton, CO



 
> 8.3.4 doesn't say for light hazard "only" and it doesn't prohibit the 
> use of small orifice sprinklers in OH. The Tyco TY-FRB is UL Listed in 
> 2.8k,4.2k, 5.6k and 8k for light and ordinary hazard. If it's Listed 
> for OH why couldn't it be used?
> 
> I would probably call the company that submitted the plans and ask for 
> supporting information like an area water main map with elevations 
> etc... With the right information the validity of the flow test could 
> be determined. It isn't unusual for a building to be near completion 
> before the extended water system is in place and ready to be tested.
> 
> Ron Fletcher
> Aero Automatic
> Phoenix, AZ


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to