Mark,

You submitted heads for testing by UL at your expense?  I've understood that 
the process is long and not real cheap.  What was the reasoning behind going to 
all that trouble? 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Phelps, Mark
Sent: Wednesday, December 02, 2009 10:17 AM
To: [email protected]
Subject: RE: Calcs-How much margin

I know this is probably a very dead horse, but several times over the past 15 
or so years, we have had sprinkler heads less than 5.6k tested by UL and list 
for use with Various brands and concentrates of AFFF for use in Group I 
Aircraft Hangars. All were reviewed and approved by their respective AHJ's.
Mark at Aero

-----Original Message-----
From: [email protected]
[mailto:[email protected]]on Behalf Of Roland Huggins
Sent: Tuesday, December 01, 2009 11:13 AM
To: [email protected]
Subject: Re: Calcs-How much margin


that's a restriction that applies only to STORAGE

Roland

On Dec 1, 2009, at 8:38 AM, Thom McMahon wrote:

> NFPA 13 has other restrictions on orifice size in OH occupancies, and 
> even 5.6K heads that are listed for OH cannot be used for design 
> densities over 0.30 GPM/SF (From memory, could be wrong #)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to