NFPA 13 has other restrictions on orifice size in OH occupancies, and even
5.6K heads that are listed for OH cannot be used for design densities over
0.30 GPM/SF (From memory, could be wrong #) Specifically because small drops
don't make it to the seat of the fire before they turn to steam.(4.2K heads
have even smaller droplets.) Steam is good for some fires like residential,
low ceilings knocks smoke down for occupant egress, indicates a good heat
exchange, ect. But in OH what good does it do if the droplet size is so
small that the steam forms 20'-0" AFF and the water never reaches the seat
of the fire. That's why we see more of the large orifice Special Application
Storage Sprinklers. K11.2, K14, K16.8, K22, K25. BIG Droplet Size penetrates
the fire better.
In this case "Bigger is Better."

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: Tuesday, December 01, 2009 7:21 AM
To: [email protected]
Subject: RE: Calcs-How much margin

If the heads "are not as effective in controlling a fire" then how do they
get UL Listed? If it is Listed and I would assume tested it should be okay
to use. If it is OH-I and the spacing requires an EHP less than
7 psi why not use the UL listed 4.2k head?

Ron Fletcher
Aero Automatic
Phoenix, AZ

 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to