You must protect the lower hazard area at the higher hazard level for 15' 
beyond where the higher hazard ends.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Tuesday, December 01, 2009 12:17 PM
To: [email protected]
Subject: QR / SR SPRINKLER SEPARATION 

I have an building where we go from an area that requires standard
response ELO sprinklers into a light hazard hallway and break room (QR
sprinklers) without any separation at the ceiling.  Is a draft curtain
required between the SR / QR sprinklers or are we ok since they are two
different hazards?  
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI