That's the problem, no separation between the two.  Do I tell the owner he 
needs to build a draft curtain (8" deep?)    
 separating the two areas? 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, December 01, 2009 12:30 PM
To: [email protected]
Subject: RE: QR / SR SPRINKLER SEPARATION 

So you've just handed him the dilemma of using SR ELO's in a light hazard 
corridor......hope people don't die.
:)
Seriously, Dwayne, I'd use the ELOs up the corridor and then switch to the QR 
in the breakroom, assuming the breakroom is separated by a wall from the high 
hazard area.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Tuesday, December 01, 2009 1:20 PM
To: '[email protected]'
Subject: RE: QR / SR SPRINKLER SEPARATION 

You must protect the lower hazard area at the higher hazard level for 15'
beyond where the higher hazard ends.

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS & MO 

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Tuesday, December 01, 2009 12:17 PM
To: [email protected]
Subject: QR / SR SPRINKLER SEPARATION 

I have an building where we go from an area that requires standard response ELO 
sprinklers into a light hazard hallway and break room (QR
sprinklers) without any separation at the ceiling.  Is a draft curtain required 
between the SR / QR sprinklers or are we ok since they are two different 
hazards?  
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to