Could be, the original flow test was from 2007, but the water utility still 
tells me this is representative of the area. 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Monday, December 14, 2009 10:49 AM
To: '[email protected]'
Subject: RE: forward flow test problem

Are there  any major users in the area?

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS & MO 

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Monday, December 14, 2009 10:46 AM
To: [email protected]
Subject: forward flow test problem

We have a job where the residual pressure recorded during the backflow test is 
lower than expected.  The hydrant used for the original water test is about 
10ft lower than the system riser and has a flow test result of 72PSI static, 
62PSI residual, flowing 902GPM (off a circulating system).  I had my fitter 
install a pressure gauge before the 1st check on the BFP and the we recorded a 
static of 67PSI but a residual of 50PSI at a flow of 715GPM.  I confirmed with 
the water utility that the gate valve for the water lead in is fully open and 
that no pumps or valves have been shut off for water main breaks or 
maintenance.  Unfortunately, they will not run a new flow test in winter.
Any ideas as to what is causing the low residual pressure?  
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to