I think this would be the most accurate solution to the problem.You can also 
test the backflow device at the same time.

LV

 
---- Dewayne Martinez <[email protected]> wrote: 
> The UG supply line is 6" plastic water pipe coming off a 10in main in the 
> street.  I thought maybe the new 6" is obstructed somehow but that should 
> have showed up during the UG flush. There is a new hydrant on the 6in lead in 
> and a wall hydrant on the backside of the building.  What does the forum 
> think about putting the gauge on the hydrant and flowing the wall hydrant out 
> the back side of the building for the flow?  This would eliminate the water 
> utilities concerns about "icing" the street and I would only have to be 
> concerned about the owners landscaping. 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Matt Grise
> Sent: Monday, December 14, 2009 10:51 AM
> To: '[email protected]'
> Subject: RE: forward flow test problem
> 
> What is the underground supply line to the system riser like? Could it be 
> causing extra pressure loss?
> 
> Matt Grisé PE*, LEED AP
> Sales Engineer
> Alliance Fire Protection
> *Licensed in KS & MO 
> 
> 913.888.0647 ph
> 913.888.0618 f
> 913.927.0222 cell
> www. AFPsprink.com 
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Dewayne 
> Martinez
> Sent: Monday, December 14, 2009 10:46 AM
> To: [email protected]
> Subject: forward flow test problem
> 
> We have a job where the residual pressure recorded during the backflow test 
> is lower than expected.  The hydrant used for the original water test is 
> about 10ft lower than the system riser and has a flow test result of 72PSI 
> static, 62PSI residual, flowing 902GPM (off a circulating system).  I had my 
> fitter install a pressure gauge before the 1st check on the BFP and the we 
> recorded a static of 67PSI but a residual of 50PSI at a flow of 715GPM.  I 
> confirmed with the water utility that the gate valve for the water lead in is 
> fully open and that no pumps or valves have been shut off for water main 
> breaks or maintenance.  Unfortunately, they will not run a new flow test in 
> winter.
> Any ideas as to what is causing the low residual pressure?  
> Thanks,
> Dewayne Martinez
> Design Build Fire Protection
> New Berlin, WI
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to