Where is the backflow device? If at the riser and that is 10 feet
higher than the test hydrant as you say then the static is correct. 72
psiI less 4.33 psi for elevation equals as close to 67 psi as I can
read on a gauge. I also plotted these results and got about 40 psi at
900 gpm. What size orifice are you flowing through? Is it the same as
was flowed on the hydrant?

On Mon, Dec 14, 2009 at 8:45 AM, Dewayne Martinez <[email protected]> wrote:
> We have a job where the residual pressure recorded during the backflow
> test is lower than expected.  The hydrant used for the original water
> test is about 10ft lower than the system riser and has a flow test
> result of 72PSI static, 62PSI residual, flowing 902GPM (off a
> circulating system).  I had my fitter install a pressure gauge before
> the 1st check on the BFP and the we recorded a static of 67PSI but a
> residual of 50PSI at a flow of 715GPM.  I confirmed with the water
> utility that the gate valve for the water lead in is fully open and that
> no pumps or valves have been shut off for water main breaks or
> maintenance.  Unfortunately, they will not run a new flow test in
> winter.
> Any ideas as to what is causing the low residual pressure?
> Thanks,
> Dewayne Martinez
> Design Build Fire Protection
> New Berlin, WI
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to