I can't find  where the UV/IR is required.Is this just the "Cadillac",I would 
think that linear heat detection would be acceptable.Is this correct?

Scott Enides
Chief Estimator
SRI Fire Sprinkler,LLC

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Saturday, December 12, 2009 12:44 PM
To: [email protected]
Subject: Re: NFPA 415 glazing protection

NFPA 415 ;2002; 4.1.5.3.1 or 4.1.5.3.1.1. the system shall be designed 
to provide a density of at least   0.25 gpm /sq ft over the exterior 
surface area of the glazing material.
Use WS window sprinklers from Central (Tyco). Use UV/IR  detectors to 
activate the deluge valve. Recommended Schedule 40 A-53 piping.
For more information contact Fred McGilvray Company  phone 
305-592-5910;j John Oliveira or Efrem Mercado. e-mail:.fmi _ mia @  
bellsouth.net

Mario berrios
ph. 305-869-1346
fax 305-869-3898
-----Original Message-----
From: Greg McGahan <[email protected]>
To: [email protected]
Sent: Fri, Dec 11, 2009 3:50 pm
Subject: RE: NFPA 415 glazing protection


Has anyone performed any work in an airport where glazing protection 
was
required?

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell(850) 554.3231
[email protected]


-----Original Message-----
 From: [email protected] 
[mailto:[email protected]]
On Behalf Of Greg McGahan
Sent: Friday, December 11, 2009 11:04 AM
To: [email protected]
Subject: NFPA 415 glazing protection

Anyone have experience with the NFPA 415 reference to NFPA 15 for
glazing protection in which 15 gives no guidance for glazing protection?

Thanks if you can help,
Greg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email 
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email 
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to