If there is an explosion on the ramp the uv/ir detectors will see the flames and they will activate the deluge valve. mario berrios
-----Original Message----- From: Scott Enides <[email protected]> To: [email protected] Sent: Wed, Dec 16, 2009 7:15 am Subject: RE: NFPA 415 glazing protection I can't find where the UV/IR is required.Is this just the "Cadillac",I would think that linear heat detection would be acceptable.Is this correct? Scott Enides Chief Estimator SRI Fire Sprinkler,LLC -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Saturday, December 12, 2009 12:44 PM To: [email protected] Subject: Re: NFPA 415 glazing protection NFPA 415 ;2002; 4.1.5.3.1 or 4.1.5.3.1.1. the system shall be designed to provide a density of at least 0.25 gpm /sq ft over the exterior surface area of the glazing material. Use WS window sprinklers from Central (Tyco). Use UV/IR detectors to activate the deluge valve. Recommended Schedule 40 A-53 piping. For more information contact Fred McGilvray Company phone 305-592-5910;j John Oliveira or Efrem Mercado. e-mail:.fmi _ mia @ bellsouth.net Mario berrios ph. 305-869-1346 fax 305-869-3898 -----Original Message----- From: Greg McGahan <[email protected]> To: [email protected] Sent: Fri, Dec 11, 2009 3:50 pm Subject: RE: NFPA 415 glazing protection Has anyone performed any work in an airport where glazing protection was required? Greg McGahan Operations Manager Living Water Fire Protection 1160 McKenzie Road P.O. Box 877 Cantonment, Florida 32533 (850) 937.1850 | Fax (850) 937.1852 | Cell(850) 554.3231 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Friday, December 11, 2009 11:04 AM To: [email protected] Subject: NFPA 415 glazing protection Anyone have experience with the NFPA 415 reference to NFPA 15 for glazing protection in which 15 gives no guidance for glazing protection? Thanks if you can help, Greg _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)
