What if I just called to say hi? Happy holidays Rich and everybody
else on the Forum.

On Tue, Dec 15, 2009 at 2:01 PM, Richardson, R <[email protected]> wrote:
> I would suggest that in this case you do not check with the AHJ.  NFPA 13 
> clearly requires sprinklers in the space, unless the wood is FR.  Personally, 
> I get annoyed with a phone call whose goal is to simply confirm what NFPA 
> clearly states.  There are plenty of off-beat situations not clearly 
> addressed by NFPA where a phone inquiry is required, this is not one of them.
>
> Rich Richardson
> Seattle Fire Department
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of njarendt 
> tds.net
> Sent: Tuesday, December 15, 2009 13:44
> To: [email protected]
> Subject: Re: Drop Wood Ceiling
>
> Check with the authority having jurisdiction.  They are the ones that
> ultimately will determine what is needed.  Contact up front with the AHJ
> usually saves a lot in the long run.  I do plan review for 2 fire districts
> and time and energy can be saved by this up front discussion on issues like
> this.
>
> Norm
> On Tue, Dec 15, 2009 at 12:53 PM, Jimmy Waite <[email protected]>wrote:
>
>> Gentlemen,
>>
>>
>>
>> We have a situation where an engineer in requiring sprinkler protection
>> above a drop wood ceiling.  The building is light hazard and
>> noncombustible,
>> and we have obviously provided protection below the ceiling.  I can't place
>> a code reference in defense of either side.  It would seem that we have
>> adequately protected the wood ceiling by protecting the floor space below
>> it.  On the other hand, the back of the wood ceiling would mean there are
>> combustibles in a concealed space.  What is everyone's opinion?
>>
>>
>>
>> Thanks,
>>
>>
>>
>> Jimmy Waite
>>
>> Design Engineer
>>
>>
>> Piedmont Fire Protection Systems, LLC
>>
>> 3609 Bastion Lane
>>
>> Raleigh, NC  27604
>>
>>
>> o: 919.212.2356
>>
>> f:  919.212.2357
>>
>>  <mailto:[email protected]> [email protected]
>>
>> web:  <http://www.piedmontfire.com/> www.piedmontfire.com
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email 
>> to:[email protected]<to%[email protected]>
>> (Put the word unsubscribe in the subject field)
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to