Thanks for the input everyone.  After a little digging we found the ceiling
was Class A fire rated.

Jimmy Waite
Design
Engineer                                                                    
       
Piedmont Fire Protection Systems, LLC                            
3609 Bastion Lane            
Raleigh, NC  27604                     
                                                                            
                      
o: 919.212.2356  
f:  919.212.2357  
[email protected]
web: www.piedmontfire.com                                                

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Wednesday, December 16, 2009 2:41 AM
To: [email protected]
Subject: RE: Drop Wood Ceiling

I agree. It is the standard that determines what is needed, not the AHJ. If
the intent of the standard is clear, a ruling by the AHJ different from the
standard will not get you off the hook. 

Sometime back an AHJ issued a bullettin permitting the installation of
exposed cpvc, contrary to the requirements of the building code that were
applicable during that time. Many buildings in that locality were installed
with exposed cpvc. Everything was fine, till a school with exposed cpvc had
a fire. To cut a long story short, the fire started at the roof, the pump
stopped working,  and the entire school burned down. However, the "expert"
hired by the owner claimed the system failed due to the burning of the
exposed cpvc pipe. In addition to the AHJ bullettin, the engineer for the
project issued an addendum permitting the use of exposed cpvc. This engineer
also provided inspections (for which I was not hired).

When the lawyer for the owner asked me why I (working for the sprinkler
contractor) designed for cpvc, I showed the addendum, and was told I was the
expert and have a responsibility to advise the engineer. When I showed the
bullettin, I was asked whether I did not know that the AHJ was not an
engineer.

Interestingly, since then that bullettin has been rescinded. Also, cpvc
(exposed or protected) is now totally prohibited for schools in that
jurisdiction.

The moral of the story is comply with the standard.

Tony     

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richardson, R
Sent: December 15, 2009 3:01 PM
To: [email protected]
Subject: RE: Drop Wood Ceiling

I would suggest that in this case you do not check with the AHJ.  NFPA 13
clearly requires sprinklers in the space, unless the wood is FR.
Personally, I get annoyed with a phone call whose goal is to simply confirm
what NFPA clearly states.  There are plenty of off-beat situations not
clearly addressed by NFPA where a phone inquiry is required, this is not one
of them.

Rich Richardson
Seattle Fire Department

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of njarendt
tds.net
Sent: Tuesday, December 15, 2009 13:44
To: [email protected]
Subject: Re: Drop Wood Ceiling

Check with the authority having jurisdiction.  They are the ones that
ultimately will determine what is needed.  Contact up front with the AHJ
usually saves a lot in the long run.  I do plan review for 2 fire districts
and time and energy can be saved by this up front discussion on issues like
this.

Norm
On Tue, Dec 15, 2009 at 12:53 PM, Jimmy Waite
<[email protected]>wrote:

> Gentlemen,
>
>
>
> We have a situation where an engineer in requiring sprinkler 
> protection above a drop wood ceiling.  The building is light hazard 
> and noncombustible, and we have obviously provided protection below 
> the ceiling.  I can't place a code reference in defense of either 
> side.  It would seem that we have adequately protected the wood 
> ceiling by protecting the floor space below it.  On the other hand, 
> the back of the wood ceiling would mean there are combustibles in a 
> concealed space.  What is everyone's opinion?
>
>
>
> Thanks,
>
>
>
> Jimmy Waite
>
> Design Engineer
>
>
> Piedmont Fire Protection Systems, LLC
>
> 3609 Bastion Lane
>
> Raleigh, NC  27604
>
>
> o: 919.212.2356
>
> f:  919.212.2357
>
>  <mailto:[email protected]> [email protected]
>
> web:  <http://www.piedmontfire.com/> www.piedmontfire.com
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%3ASprinklerforum-reques
> [email protected]> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to