Yo forumites,
 
Bonding is not easy too define in an exact way as totally different from 
grounding.  The difference is in the purpose.  
 
-Don't ground something to the sprinkler system that may make the sprinkler 
system become charged.
 
-Do bond the system to the building and the lightning protection system where 
required.
 
Bonding means that if a small electrcal currents build up within or hit the 
building (or the sprinkler system), that the current would made less dangerous 
by "sharing" it with the rest of the building and it's systems.  Now this is a 
very simplistic explanation and not worthy of sharing with your electrician 
friends.  
 
Full bonding of the sprinkler system is nearly impossible and often 
misunderstood and misapplied.  Just ensure with the electrician that they have 
not "grounded" a system to the sprinkler piping.  
 
Good clue for the real world:  If there is a single small wire going from a 
panel cover or a JB (junction box) to the sprinkler system (or even a series of 
small wires), that is likely an effort at bonding.  If there is a major wire 
going from inside a panel or from a large rod to the sprinkler system, someone 
has lkely misunderstood the whole grounding/bonding issue.

And don't try to get involved with the bonding stuff.  EXCLUDE IT FROM ALL OF 
YOUR WORK!!  Cause, as I said, it is nearly impossible to fully bond the 
sprinkler system as a single unit to the building.
 


It should be recognized that the above is my opinion as a member of the NFPA 13 
Committee on Installation Criteria, and has not been processed as a formal 
interpretation in accordance with the NFPA Regulations Governing Committee 
Projects and should therefore not be considered, nor relied upon, as the 
official position of the the NFPA, nor any of their technical committees.

Sincerely,


Cecil Bilbo
Academy of Fire Sprinkler Technology
Champaign, IL
217-363-2460
www.sprinkleracademy.com






----------------------------------------
> Subject: Bonding of sprinkler systems
> Date: Mon, 21 Dec 2009 09:40:20 -0800
> From: st...@protectiondesign.com
> To: sprinklerforum@firesprinkler.org
>
> All:
>
> There is a current thread on another list that we subscribe to regarding
> electrical bonding of sprinkler systems. The cited reference is NEC
> 250.104 Bonding of Piping Systems and Exposed Structural Steel; since I
> have always subscribed to the "Let Sparky do the wiring" school of
> electrical design and coordination, I really don't know what the hell
> that means or how it's intended to be carried out. Can anyone shed
> light on what "bonding" is - as opposed to grounding - and what the
> accepted practice(s) is(are) WRT to getting it done? Have never
> undertaken that, like, never ever and the electrical code simply says
> "piping systems", not sprinklers specifically ...
>
> Steve Leyton
>
> PROTECTION DESIGN & CONSULTING
>
> ***** Please Note Our New Address *****
>
> 2851 Camino del Rio South, Suite 400
>
> San Diego, CA 92108
>
> -------------------------------------------------------------
>
> Ph: 858.751.2930 - ext. 102
>
> Fax: 858.751.2933
>
> Cell: 619.972.5696
>
>
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: supp...@firesprinkler.org
>
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)                               
>           
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to