Cecil - you handsome devil you:

So ...   how well can that work when (presuming diligence) we have a
concurrent effort to completely separate the sprinkler system from
ground.   Say I specify or install a dielectric flange gasket at the POE
- how does that effect bonding or does it even affect it at all?

Steve Leyton
Protection Design & Consulting
San Diego, CA



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Sprinkler
Academy - C Bilbo
Sent: Monday, December 21, 2009 11:10 AM
To: FORUM
Subject: RE: Bonding of sprinkler systems


Yo forumites,
 
Bonding is not easy too define in an exact way as totally different from
grounding.  The difference is in the purpose.  
 
-Don't ground something to the sprinkler system that may make the
sprinkler
system become charged.
 
-Do bond the system to the building and the lightning protection system
where required.
 
Bonding means that if a small electrcal currents build up within or hit
the
building (or the sprinkler system), that the current would made less
dangerous by "sharing" it with the rest of the building and it's
systems.
Now this is a very simplistic explanation and not worthy of sharing with
your electrician friends.  
 
Full bonding of the sprinkler system is nearly impossible and often
misunderstood and misapplied.  Just ensure with the electrician that
they
have not "grounded" a system to the sprinkler piping.  
 
Good clue for the real world:  If there is a single small wire going
from a
panel cover or a JB (junction box) to the sprinkler system (or even a
series
of small wires), that is likely an effort at bonding.  If there is a
major
wire going from inside a panel or from a large rod to the sprinkler
system,
someone has lkely misunderstood the whole grounding/bonding issue.

And don't try to get involved with the bonding stuff.  EXCLUDE IT FROM
ALL
OF YOUR WORK!!  Cause, as I said, it is nearly impossible to fully bond
the
sprinkler system as a single unit to the building.
 


It should be recognized that the above is my opinion as a member of the
NFPA
13 Committee on Installation Criteria, and has not been processed as a
formal interpretation in accordance with the NFPA Regulations Governing
Committee Projects and should therefore not be considered, nor relied
upon,
as the official position of the the NFPA, nor any of their technical
committees.

Sincerely,


Cecil Bilbo
Academy of Fire Sprinkler Technology
Champaign, IL
217-363-2460
www.sprinkleracademy.com






----------------------------------------
> Subject: Bonding of sprinkler systems
> Date: Mon, 21 Dec 2009 09:40:20 -0800
> From: st...@protectiondesign.com
> To: sprinklerforum@firesprinkler.org
>
> All:
>
> There is a current thread on another list that we subscribe to
regarding
> electrical bonding of sprinkler systems. The cited reference is NEC
> 250.104 Bonding of Piping Systems and Exposed Structural Steel; since
I
> have always subscribed to the "Let Sparky do the wiring" school of
> electrical design and coordination, I really don't know what the hell
> that means or how it's intended to be carried out. Can anyone shed
> light on what "bonding" is - as opposed to grounding - and what the
> accepted practice(s) is(are) WRT to getting it done? Have never
> undertaken that, like, never ever and the electrical code simply says
> "piping systems", not sprinklers specifically ...
>
> Steve Leyton
>
> PROTECTION DESIGN & CONSULTING
>
> ***** Please Note Our New Address *****
>
> 2851 Camino del Rio South, Suite 400
>
> San Diego, CA 92108
>
> -------------------------------------------------------------
>
> Ph: 858.751.2930 - ext. 102
>
> Fax: 858.751.2933
>
> Cell: 619.972.5696
>
>
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: supp...@firesprinkler.org
>
> To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4706 (20091221) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4706 (20091221) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to