Roland, Is there a specific section that lists these variables or were you just talking in general? I thought I was thorough in my water system evaluation. I verified through the city engineer that no valves were closed, no pumps were off, no main breaks at time of BFP test, and that the water tower was not lowered for winter conditions. Anything else I should have checked? The kicker is when you get a water flow test from the water department, there is a disclaimer that the readings may be off by +/- 15PSI! Too bad the fire department only requires a 5PSI or 10% cushion, whatever is greater. It is hard to be competitive if we have to design to a 15PSI cushion for this city. Thanks, Dewayne
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Tuesday, December 22, 2009 10:17 AM To: [email protected] Subject: Re: forward flow test problem I never saw a word regarding conducting an evaluation of variables that can impact the water supply (listed in NFPA 13). Performing a single water flow test is only the starting point in determining the available water supply. It gets quite interesting when a secondary pumps kick in such that the residential pressure is higher than the static. Roland On Dec 15, 2009, at 4:28 AM, Dewayne Martinez wrote: > Thanks, > I am going to have a meeting with the inspector and water department > to try and come up with a resolution to the issue. Thanks for > everyone's input, as always, invaluable. > Dewayne > > Subject: forward flow test problem > To: [email protected] > Date: Monday, December 14, 2009, 10:45 AM _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)