Since I assume you're doing an NFPA 25 inspection, and your within the
allowed 10% variance, I'd note it on both the riser and in the
inspection form, and move on. If you don't meet the 10% next year I'd
start all the flow testing ect. Which your contemplating now.

If you really feel you need to do more now, I'd throttle your flow back
to
252 Gpm and verify the residual. I think you'll find it much closer to
the hydraulic demand, at the inlet to the BFP.(Base of riser)

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Monday, December 14, 2009 12:24 PM
To: [email protected]
Subject: RE: forward flow test problem

The worst case is 252GPM @ 59 PSI with no inside hose.  When I plot this
on the adjusted water curve it is below the curve but does not meet the
10% minimum safety factor required. I think I will try to run a new flow
test to try and get to the bottom of things.  


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to