Since I assume you're doing an NFPA 25 inspection, and your within the
allowed 10% variance, I'd note it on both the riser and in the inspection
form, and move on. If you don't meet the 10% next year I'd start all the
flow testing ect. Which your contemplating now.

If you really feel you need to do more now, I'd throttle your flow back to
252 Gpm and verify the residual. I think you'll find it much closer to the
hydraulic demand, at the inlet to the BFP.(Base of riser)