Steve

The following in my official capacity:

Biodiesel will generate some degree of 'fermentation' in the tank.  The longer 
it is stored, the more decay there will be and a greater chance of 
contamination of the fuel lines of an engine.

Tyco have done some work on this and are presently seeking support for a 
campaign in Europe to make sure non-bio diesel remains available - a number of 
national governments are imposing % targets of biofuel in diesel and gasoline 
on fuel suppliers.

The issue is more critical for fire pumps and stand-by generators (than for 
road vehicles)as here is a greater probability that the fuel will sit in the 
tank for a long time.  There have reportedly been a couple of cases where fire 
pumps have failed to start due to clogged filters.

Regards

Stewart

Stewart Kidd
Secretary General

British Automatic Fire Sprinkler Association Ltd
Registered in England in 1974: No 01194637 as a company limited by guarantee
Richmond House, Broad Street, Ely  CB7 4AH
Tel 01353 659187, Fax 01353 666619
Email [email protected]

UK Insurers have issued the following guidance through RISCA/FPA:

Guidance Note - Diesel Fuel for Automatic Fire Sprinkler Pumps
 
Diesel fuel with a percentage of FAME (Fatty Acid Methyl Ester) content derived 
from crops is increasingly becoming available in the fuel supply chain in the 
UK, Europe and other regions of the world. Diesel fuels containing a proportion 
of FAME are often called “Biofuels” or “Biodiesels”. In the UK there are 
legislative requirements for fuels for road use to have some FAME content. We 
have been advised by the Department for Transport that these requirements for a 
percentage FAME content do not apply to stationary equipment such as automatic 
fire sprinkler pumps (and emergency generators).
 
Fuels with FAME content, when compared to hydrocarbon only fuels may have a 
reduced life. Engines may require additional maintenance at increased 
frequencies and are likely to experience reduced power output even when running 
optimally. The frequencies and nature of maintenance will depend upon the 
engine, percentage FAME content of fuel and quality of the fuel.
 
The manufacturers of the diesel drivers for use in automatic fire sprinkler 
pumps in the UK specify that their equipment is suitable for use with fuels to 
BS 2869 Class A2, which currently allows up to 5% FAME content (expressed as 
“B5” for 5%). It is worth noting that BS 2869 Class A2 with zero % FAME content 
is still widely available in UK.
 
Advice from fuel suppliers about how long their fuel may be stored in a fuel 
tank varies. BS 2869 Class A2 at up to 5% FAME content was said to be suitable 
for storage for between 6-18 months depending on the fuel quality and ambient 
storage conditions. Generally, higher levels of FAME content decrease the 
stability of fuel and therefore storage duration.
 
Advice to users of automatic diesel fire pumps from the FPA is:
 
·       Use a quality fuel from a reputable supplier;
·       Use fuel with the lowest FAME content possible[1];
·       Ensure maintenance of pump set & driver is undertaken as specified by 
the equipment manufacturer and by a competent person;
·       Ensure all clauses of TB203 “Care and Maintenance of Automatic 
Sprinkler Systems” of the “LPC Rules for Automatic Sprinkler Installations 
(2009)” are followed[2]; and
·       Avoid storing fuels for excessive periods (period depends on fuel type 
and quality – check with supplier)
 
FPA will continue to monitor the situation. If the above advice and that of the 
pump supplier is followed and problems are encountered, please advise the FPA 
([email protected]) of your experience so that we may review and update 
our advice in time if necessary.  
 
 
FPA, 14th December 2009.

[1] At the time of publication, zero percent FAME content fuel was available. 
Note that pumps using diesel fuel with zero percent FAME content will still 
require maintenance as specified by the pump set manufacturer and TB203.

 

[2] The weekly testing requirements should be strictly followed to ensure the 
pump remains in good working order and also to generate fuel turn over

 



On 22 Dec 2009, at 16:30, Steve Leyton wrote:

> All:
> 
> 
> 
> Anyone have any idea whether or not diesel pump engines are tolerant of
> the three families (some would say four) of diesel fuel without issues?
> I was asked whether it would be a problem to run a typical pump on
> biodiesel, low sulfur or ultra-low sulfur diesel and haven't heard this
> talked about like, at all.
> 
> 
> 
> Steve Leyton
> 
> PROTECTION DESIGN & CONSULTING
> 
> ***** Please Note Our New Address *****
> 
> 2851 Camino del Rio South, Suite 400
> 
> San Diego, CA 92108
> 
> -------------------------------------------------------------
> 
> Ph:      858.751.2930 - ext. 102
> 
> Fax:    858.751.2933
> 
> Cell:  619.972.5696
> 
> 
> 
> 
> 
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to