Right.   Maybe we need a sign at the filler connection as on automobiles
stating, "Use #2 Diesel only" or whatever.   Or put, "Fuel by others"
onto the list of standard-form exceptions ...  No wiring, no paint, no
extinguishers, fuel by others.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Tuesday, December 22, 2009 1:29 PM
To: [email protected]
Subject: RE: Bio-diesel in pump drivers

You forgot the part about making sure the next guy who fills the tank
fills
it with the right grade. 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Tuesday, December 22, 2009 3:24 PM
To: [email protected]
Subject: RE: Bio-diesel in pump drivers

Thanks Stewart.   Since posting the question this morning, I have
learned that storage stability is the key concern.   The drivers
themselves can be built and the ECM's programmed to run on any fuel, but
the problem with the biodiesel is the long-term quality of the oil.   In
California, all engines - per state air quality standards, can you
believe it? - have to run on ultra-low sulfur, but it's  petroleum and
not vegetable based, so storage is viable.   The answer to this question
appears to be that we now have to specify the type of fuel when ordering
the driver, verify that the engine output doesn't have to be de-rated up
to 10% as it might be if you're running a driver designed for #2 on red
diesel or #1, have the rep verify that you're compliant with the air
quality laws of your state.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Stewart
Kidd
Sent: Tuesday, December 22, 2009 11:03 AM
To: [email protected]
Subject: Re: Bio-diesel in pump drivers

Steve

The following in my official capacity:

Biodiesel will generate some degree of 'fermentation' in the tank.  The
longer it is stored, the more decay there will be and a greater chance
of contamination of the fuel lines of an engine.

Tyco have done some work on this and are presently seeking support for a
campaign in Europe to make sure non-bio diesel remains available - a
number of national governments are imposing % targets of biofuel in
diesel and gasoline on fuel suppliers.

The issue is more critical for fire pumps and stand-by generators (than
for road vehicles)as here is a greater probability that the fuel will
sit in the tank for a long time.  There have reportedly been a couple of
cases where fire pumps have failed to start due to clogged filters.

Regards

Stewart

Stewart Kidd
Secretary General

British Automatic Fire Sprinkler Association Ltd
Registered in England in 1974: No 01194637 as a company limited by
guarantee
Richmond House, Broad Street, Ely  CB7 4AH
Tel 01353 659187, Fax 01353 666619
Email [email protected]

UK Insurers have issued the following guidance through RISCA/FPA:

Guidance Note - Diesel Fuel for Automatic Fire Sprinkler Pumps
 
Diesel fuel with a percentage of FAME (Fatty Acid Methyl Ester) content
derived from crops is increasingly becoming available in the fuel supply
chain in the UK, Europe and other regions of the world. Diesel fuels
containing a proportion of FAME are often called "Biofuels" or
"Biodiesels". In the UK there are legislative requirements for fuels for
road use to have some FAME content. We have been advised by the
Department for Transport that these requirements for a percentage FAME
content do not apply to stationary equipment such as automatic fire
sprinkler pumps (and emergency generators).
 
Fuels with FAME content, when compared to hydrocarbon only fuels may
have a reduced life. Engines may require additional maintenance at
increased frequencies and are likely to experience reduced power output
even when running optimally. The frequencies and nature of maintenance
will depend upon the engine, percentage FAME content of fuel and quality
of the fuel.
 
The manufacturers of the diesel drivers for use in automatic fire
sprinkler pumps in the UK specify that their equipment is suitable for
use with fuels to BS 2869 Class A2, which currently allows up to 5% FAME
content (expressed as "B5" for 5%). It is worth noting that BS 2869
Class A2 with zero % FAME content is still widely available in UK.
 
Advice from fuel suppliers about how long their fuel may be stored in a
fuel tank varies. BS 2869 Class A2 at up to 5% FAME content was said to
be suitable for storage for between 6-18 months depending on the fuel
quality and ambient storage conditions. Generally, higher levels of FAME
content decrease the stability of fuel and therefore storage duration.
 
Advice to users of automatic diesel fire pumps from the FPA is:
 
*       Use a quality fuel from a reputable supplier;
*       Use fuel with the lowest FAME content possible[1];
*       Ensure maintenance of pump set & driver is undertaken as
specified by the equipment manufacturer and by a competent person;
*       Ensure all clauses of TB203 "Care and Maintenance of Automatic
Sprinkler Systems" of the "LPC Rules for Automatic Sprinkler
Installations (2009)" are followed[2]; and
*       Avoid storing fuels for excessive periods (period depends on
fuel type and quality - check with supplier)
 
FPA will continue to monitor the situation. If the above advice and that
of the pump supplier is followed and problems are encountered, please
advise the FPA ([email protected]) of your experience so that we
may review and update our advice in time if necessary.  
 
 
FPA, 14th December 2009.

[1] At the time of publication, zero percent FAME content fuel was
available. Note that pumps using diesel fuel with zero percent FAME
content will still require maintenance as specified by the pump set
manufacturer and TB203.

 

[2] The weekly testing requirements should be strictly followed to
ensure the pump remains in good working order and also to generate fuel
turn over

 



On 22 Dec 2009, at 16:30, Steve Leyton wrote:

> All:
> 
> 
> 
> Anyone have any idea whether or not diesel pump engines are tolerant
of
> the three families (some would say four) of diesel fuel without
issues?
> I was asked whether it would be a problem to run a typical pump on
> biodiesel, low sulfur or ultra-low sulfur diesel and haven't heard
this
> talked about like, at all.
> 
> 
> 
> Steve Leyton
> 
> PROTECTION DESIGN & CONSULTING
> 
> ***** Please Note Our New Address *****
> 
> 2851 Camino del Rio South, Suite 400
> 
> San Diego, CA 92108
> 
> -------------------------------------------------------------
> 
> Ph:      858.751.2930 - ext. 102
> 
> Fax:    858.751.2933
> 
> Cell:  619.972.5696
> 
> 
> 
> 
> 
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4710 (20091222) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to