Look at 2.1.7
Provide sprinkler protection in concealed areas, such as attics.........

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
** Note new email address: [email protected]
 
-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of David Blackwell
Sent: Friday, February 05, 2010 12:55 PM
To: [email protected]
Subject: FM Global Data Sheet 2-5

The scope of the data sheet in 1.0 says: 

"These recommendations do not conflict with internationally recognized
residential sprinkler standards (including NFPA 13D), except in the
matter of sprinkler density and design area."

It doesn't mention changing the water supply duration which is normally
10 minutes [or 7 minutes if a single story building and less than 2000
sq. ft.] per NFPA 13D.

I note that they require 60 minutes of water supply duration in 2.1.4.2:

"2.1.4.2 Ensure the sprinkler system is capable of supplying the total
system water demand for a minimum duration of 60 minutes."
 
It looks like this would negatively impact the cost of systems in rural
areas.




David W. S. Blackwell, II, PE, CFI-I, CFPE
Engineering 
---------------------------------------------------------------- 
Office of State Fire Marshal 
141 Monticello Trail 
Columbia, SC 29203 
Phone:  803.896.9833 
Fax:  803.896.9806 
Email:  [email protected] 
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp 
---------------------------------------------------------------- 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of tom
poisal
Sent: Friday, February 05, 2010 12:35 PM
To: [email protected]
Subject: Re: help the NAHB!

For those interested; FM Global just published Data sheet 2-5,
Installation
Guidelines For Automatic Sprinklers in Residential Occupancies, might be
fuel for the fire!


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to