I won't disagree with your statement of theory but we have a very long
history of sprinkler success.  The rules whether related to wetting the
floor or plume dynamics are well tested.  We simply don't have failures when
complying with the code.  The code says you don't have to space to this beam
given compliance with the tables.  Ok maybe there are 1 or 2 failures out
there but I'll take that over 100+ years. And so what if the farther away
heads go first.  We calc 5 minimum and usually much more.  Look at some of
the testing in HPS.  When ignition is between 4 sometimes all 4 don't even
go off. We are aiming for control not suppression (except ESFR).  In reality
we actually achieve suppression a vast majority of the time. 

If you want to up the stakes to suppression on the first head you sure could
run CFD models but even they are not definitive.  And what do we gain?  And
the cost of CFD modeling?  And the manipulation of data and models and
limitation of models for an agenda, can we say man induced global warming?
We don't have enough people that can apply NFPA 13 properly now add CFD
modeling? 

Now on to the legal matter of code enforcement, which is a criminal matter,
if the legal enforcer i.e. fire marshal (vs. the generic AHJ that includes
others like insurance) can't point to a section where you are not in
compliance that's the end of the story.  They can jump up and down and
recite all the research in existence and even produce a CFD model showing
failure.  In the end if I've met the letter NFPA 13 I'm clear legally.  True
if there was ever a failure I might have a civil problem.   NFPA 13 8.1.1
(3) is absolutely unenforceable in law.  Now where is it defined what is
satisfactory performance.  We simple don't operate in a performance
environment.  Most likely never will.  (5) implies IMHO the clearance
requirements of the standard take into account satisfactory ability to
control or suppress the fire.  You have to have satisfactory activation to
get satisfactory control.  And everything in an annex is not enforceable
either unless specifically adopted by the legal authority. 

Oh and welcome to the non-lurking club.  It's a mix of friendly help,
spirited discussion and the very rare argument.  We can get a little
friendly at times because some of us have been here for over 10 years.  Many
have met in person and some get together on a regular basis.  While a
certain person complained about the friendly nature on a professional forum
we say BS it doesn't have to be all stuffy.  About the only topic we avoid
is the PE vs. tech debate and all PE's on the forum know when generic PE's
are bashed it's those not here.          

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Michael J.
Ricks
Sent: Thursday, February 11, 2010 8:04 AM
To: [email protected]
Subject: Beam obstruction rules

It really depends on the location of the fire plume in relationship to the
heads and where the jet will be directed by the roof/ceiling elements.  When
I said the AHJ "may" have a point.  I was responding in the hypothetical.
It the original post the second head would have been 10' away from the first
beam and 19' away from the wall.  Since fire plumes go straight up and then
outward, if the fire were 11' feet away from the wall, two feet away from
the first beam, chances are the first head located on the other side of the
beam which is covering that part of the floor would not fuse.  I assumed
that there were more heads spaced along in the same beam pockets all spaced
the same distance away from the wall.  My guess is the row of heads 19 feet
away from the wall and 8' away from the fire plume in the second beam pocket
would all fuse before the head that is only six feet away.  We also don't
know what's past the second beam-since he said beam and not wall, what's
happening past that point.  I would need to see the plans to know what I
really felt.  My point is that just because you meet deflector distance (I
do realize that his deflectors are less than 12" per the unobstructed rules)
and obstruction rules, based on 8.1.1 and the fact that NFPA 13 doesn't
address heads above the bottom of beams in unobstructed construction, your
design may still be deficient when you look at the head layout in relation
to fire sprinkler performance theory.  
 
As sprinkler designers, we often fall into the trap of thinking covering the
floor area is what is most important.  It is very important to look at our
designs with regard to response time as well.  Where will the heat go when
there is a fire?  Unfortunately, fires don't always start directly below our
sprinkler heads. Unless there is a breeze in the building, the heat will go
straight up and then outward from there.  If there is nothing to cause it to
collect it will follow the path of least resistance.  It doesn't care if
there is a sprinkler head 6 feet away on the other side of a beam.  It might
as well be a wall.  
 
Personally, I would ere on the side of caution and space to the beams in
this case. 
 
Mike Ricks
Katco Fire Sprinkler Design
 
Interesting analysis and welcome to the jungle. However, if you read 
the handbook commentary it would seem that your concern about ceiling 
jets is addressed in the definitions of obstructed and unobstructed 
construction. I am far from an expert on the behavior of ceiling 
jets, but I would think in this situation as described, that the 
sprinklers as positioned, especially in a 17 ft span, would be within 
that jet.
 
 
At 09:52 PM 2/10/2010, you wrote:
>Not to be the contrarian here, this being my first post to this forum, but,
>I believe the AHJ has a point.
> 
> 
> 
>Given your beam spacing of over 7'-6" on center, you are dealing with
>unobstructed construction here.  NFPA 13 8.6.4.1.2, regarding placing the
>deflector above the bottom of the structural member, relates to obstructed
>construction.  In obstructed construction, we are able to place deflectors
>up to 22" below roof decks since the obstructions help collect heat to
>assure prompt activation of the sprinkler head.  (If you remember your
older
>versions of NFPA 13, we used to have to deal with the "panelized roof
>limitations of 300 square feet to get the added deflector distance.)  NFPA
>13 doesn't specifically address the issue of placing the deflector above
the
>beam in unobstructed construction and although you are meeting the
>obstruction requirements of 8.6.5.1.2, the issue here is response time.
>8.1.1 (2) states "Sprinklers shall be positioned and located so as to
>provide satisfactory performance with respect to activation time and
>distribution."  A8.1 also says "The installation requirements are specific
>for the normal arrangement of structural members.  There will be
>arrangements of structural members not specifically detailed by the
>requirements."  Just because your head is not obstructed and you have met
>the deflector distance requirements for unobstructed construction doesn't
>mean it will work as intended.
> 
> 
> 
>The theory behind automatic sprinkler performance requires that the head be
>in the jet stream or in a pocket that will collect heat in a timely manner.
>With limited obstructions to collect heat, that distance will be 5 to 12%
of
>the height of the ceiling above the fire source.   This is the theory
behind
>the 12" deflector distance rule for unobstructed construction.  Given the
>language of NFPA A8.1 and 8.1.1 the AHJ is not off base in being concerned
>with response times.  Unless you have a 30'+ ceiling, I would have concerns
>that the jet stream would be cut off by the beams and that the heat would
>not collect fast enough to assure prompt activation of the head and/or
>skipping would occur causing head outside of the fire area to activate
prior
>to heads in and around the fire area due to the jet stream being directed
>away from those heads by the beams.
> 
> 
> 
>Michael Ricks
> 
>Katco Fire Sprinkler Design
> 
>P.O. Box 607
> 
>555 South 100 East
> 
>Salem, UT   84653
> 
>801-423-3096  Cell:  801-380-4651
> 
>mike at fire-sprinkler-design.com
<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 
> 
> 
> 
> 
> 
>_______________________________________________
>Sprinklerforum mailing list
>Sprinklerforum at firesprinkler.org
<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
>For Technical Assistance, send an email to: support at firesprinkler.org
<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 
> 
>To Unsubscribe, send an email to:Sprinklerforum-request at
firesprinkler.org
<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 
>(Put the word unsubscribe in the subject field)
 
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  

 

 

Michael Ricks

Katco Fire Sprinkler Design

P.O. Box 607

555 South 100 East

Salem, UT   84653

801-423-3096  Cell:  801-380-4651

[email protected]

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to