Per NFPA 13 2010 7.6.3.4 a listed 1/2' RELIEF VALVE shall be permitted in
lieu of an expansion chamber  required in 7.6.3.3 provided antifreeze volume
does not exceed 40 Gallons, see figure 7.6.3.4

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Thursday, February 11, 2010 1:08 PM
To: [email protected]
Subject: AF Expansion Tanks

Anyone got a source for correct ones that aren't so expensive.  100 psi 5
gal about $70 (plumbers version).  2.5 gal from Firetrol(?) or Youngs in the
$600+ range.  Is this what you've been doing on AF systems?  My supplier
tells me they sell a lot of the plumber's versions and almost none of the
correct ones.  And yet I don't hear of problems.  Could be my hearing, could
be no problems. 

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [email protected]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to