We don't use perforated pipe hanger stuff cause the code doesn't allow it
for our work. Except in 13D, same holds true of expansion tanks, whether
they are made of 250 PSI WWP or not, the real question is - are they listed
as required by 13 or 13R?

The only wiggle room is what might become APPROVED if submitted, i.e., found
acceptable to the AHJ. And I doubt that a failure would be covered by his
GL.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Friday, February 12, 2010 9:09 AM
To: [email protected]
Subject: RE: AF Expansion Tanks

Not taking listed vs. unlisted. They may be as good but the cheap versions
are only listed to 100 psi.  It doesn't take a lot of temperature change to
exceed 100 psi.  And in this case I have 115 static.  And even if I had the
more typical 50 psi the general requirement is everything on the system side
of a sprinkler system must be listed to 175.  If a compressor fails at any
point including during a fire it's not a big deal.  If one responds to the
low air alarm nothing happens.  If they ignore the low air alarm the system
trips until the water gets to freezing conditions it will still put out a
fire and doesn't break the piping causing water on the ground. An expansion
tank fails and you have a big mess to report to your insurance company and
if it's only listed to 100 psi you will be paying for the loss.  If listed
to 175 you have a fighting chance to avoid payment.    

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, February 11, 2010 6:06 PM
To: [email protected]
Subject: RE: AF Expansion Tanks

Everything I have looked at says that the "cheap" ones are as good as
the listed ones. We have NEVER used a non-listed one outside of 13D but
I certainly do think it is ridiculous that an air compressor does not
have to be listed but an expansion chamber does? 
Greg

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Thursday, February 11, 2010 2:30 PM
To: [email protected]
Subject: RE: AF Expansion Tanks

13

Chris 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom
McMahon
Sent: Thursday, February 11, 2010 2:05 PM
To: [email protected]
Subject: RE: AF Expansion Tanks

13 or 13D?

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Thursday, February 11, 2010 1:08 PM
To: [email protected]
Subject: AF Expansion Tanks

Anyone got a source for correct ones that aren't so expensive.  100 psi
5 gal about $70 (plumbers version).  2.5 gal from Firetrol(?) or Youngs
in the $600+ range.  Is this what you've been doing on AF systems?  My
supplier tells me they sell a lot of the plumber's versions and almost
none of the correct ones.  And yet I don't hear of problems.  Could be
my hearing, could be no problems. 

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [email protected]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to