True the code might give you guidance. But the more fundamental is who is intended to use the standpipe. Untrained people - Class II, FD only - Class I, either - Class III. And if it's FD the spacing, pressure and size is up to them especially if not in USA. In other words maybe the FD would like more pressure than they can normally provide. OK maybe not an issue with a 2 story but who knows other than the FD and the designing professional.
Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ing. Levent Numanoglu Sent: Wednesday, February 17, 2010 6:38 PM To: [email protected] Subject: Help Hello all, I am trying to figure out which class of stand pipe system to use for a multi detached building site. There are about 5 - 2 storey non-sprinkled buildings from a single water supply from a clean water cistern. Each building is supplied with a single standpipe in a central location within a 100 feet away from the furthest point. Each building is a part of a prison with individual cells. Any help would be greatly appreciated. Thanks, Levent _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)