True the code might give you guidance.  But the more fundamental is who is
intended to use the standpipe.  Untrained people - Class II,  FD only -
Class I, either - Class III.  And if it's FD the spacing, pressure and size
is up to them especially if not in USA.  In other words maybe the FD would
like more pressure than they can normally provide.  OK maybe not an issue
with a 2 story but who knows other than the FD and the designing
professional.      

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ing. Levent
Numanoglu
Sent: Wednesday, February 17, 2010 6:38 PM
To: [email protected]
Subject: Help

Hello all, 

 

I am trying to figure out which class of stand pipe system to use for a
multi detached building site. There are about 5 - 2 storey non-sprinkled
buildings from a single water supply from a clean water cistern.  Each
building is supplied with a single standpipe in a central location within a
100 feet away from the furthest point. Each building is a part of a prison
with individual cells.  

Any help would be greatly appreciated. 

Thanks,

Levent

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to