Hello all once again and thank you for the valuable time and answers. Ron as
you mentioned, yes the prison facility and where my office is in Mexico but
I am in the city and the facility is in the middle of nowhere. 
I will definitely discuss the points which you have outlined about the
evacuation plans. At this point the constructer is looking for a solution of
Fire Protection without sprinkler system, they definitely will not put a
sprinkler system its just going to be hose connections. So I am going
between the Class II and the Class III system. And the untrained personal
will have to use the standpipe - hose station in case of a fire as the FD
will probably arrive there after the fire is out. 

Ing.Levent Numanoglu

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: jueves, 18 de febrero de 2010 08:56 a.m.
To: [email protected]
Subject: RE: Help

True the code might give you guidance.  But the more fundamental is who is
intended to use the standpipe.  Untrained people - Class II,  FD only -
Class I, either - Class III.  And if it's FD the spacing, pressure and size
is up to them especially if not in USA.  In other words maybe the FD would
like more pressure than they can normally provide.  OK maybe not an issue
with a 2 story but who knows other than the FD and the designing
professional.      

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ing. Levent
Numanoglu
Sent: Wednesday, February 17, 2010 6:38 PM
To: [email protected]
Subject: Help

Hello all, 

 

I am trying to figure out which class of stand pipe system to use for a
multi detached building site. There are about 5 - 2 storey non-sprinkled
buildings from a single water supply from a clean water cistern.  Each
building is supplied with a single standpipe in a central location within a
100 feet away from the furthest point. Each building is a part of a prison
with individual cells.  

Any help would be greatly appreciated. 

Thanks,

Levent

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to