I am working on a classroom building with cloud ceilings in each of the classrooms. Construction is concrete on steel beams. Sprinklers are to be installed bothabove and below the cloud. The space between the ceiling and the deck is 2'-6". 8.15.1.6 calls for concealed space sprinklers in combustible concealed spaces of 3'-0" of less. Am I correct in assuming that I can use regular upright sprinklers in this situation since the space in not combustible?
Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)