I am not sure this qualifies as a combustible concealed space (combustible 
enclosure being key words) as much as a ceiling mounted obstruction.  Your 
situation leads me more along the lines of the obstruction rules (8.6.5.3-2007).

8.15.1.6 also specifically calls out wood truss/joist/double wood joist..also a 
disqualifier for your described situation.


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Thursday, February 18, 2010 1:13 PM
To: [email protected]
Subject: Spklr in non comb space

I am working on a classroom building with cloud ceilings in each of
the classrooms. Construction is concrete on steel beams. Sprinklers
are to be installed bothabove and below the cloud. The space between
the ceiling and the deck is 2'-6". 8.15.1.6 calls for concealed space
sprinklers in combustible concealed spaces of 3'-0" of less. Am I
correct in assuming that I can use regular upright sprinklers in this
situation since the space in not combustible?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

--
ExchangeDefender Message Security: Click below to verify authenticity
http://www.exchangedefender.com/verify.asp?id=o1IMe7vj012375&[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to