Oh yeah. I forgot about that part (insert ironic emoticon here)

On Thu, Feb 25, 2010 at 6:56 AM, Greg McGahan <[email protected]> wrote:
> Good idea, if only sprinklers were for life safety.
>
> Greg McGahan
>
> Living Water Fire Protection
>  (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Ron Greenman
> Sent: Thursday, February 25, 2010 8:55 AM
> To: [email protected]
> Subject: Re: pull stations
>
> More reliable also which is probably why the AHJ wants the electrics
> to be monitored. What if you use a normally closed, continuous duty
> solenoid so that on loss of power the system floods. Failsafe.
>
> On Thu, Feb 25, 2010 at 5:55 AM, Greg McGahan <[email protected]> wrote:
>> Probably, but it was not my choice.
>>
>> Greg McGahan
>>
>> Living Water Fire Protection
>>  (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>>
>>
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of George Church
>> Sent: Thursday, February 25, 2010 7:36 AM
>> To: [email protected]
>> Subject: RE: pull stations
>>
>> Would pneumatic release be simpler? 1/2" galv can't be all that different
>> than conduit.
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Greg McGahan
>> Sent: Thursday, February 25, 2010 8:24 AM
>> To: [email protected]
>> Subject: RE: pull stations
>>
>> UNLESS, the AHJ requires the wiring to be monitored.
>>
>> Greg McGahan
>>
>> Living Water Fire Protection
>>  (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of
>> [email protected]
>> Sent: Thursday, February 25, 2010 7:22 AM
>> To: [email protected]
>> Subject: RE: pull stations
>>
>> That being the case I'd have to say that those pull stations have nothing to
>> do with NFPA 72.  You wouldn't need to supervise the PA wiring.  I've had
>> this type of scenario played out many times in unheated process buildings.
>> We typically use dry pipe valves, it's just simpler.
>>
>>
>> Craig L. Prahl, CET
>> Fire Protection Specialist
>> Mechanical Department
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> PO Box 491, Spartanburg, SC  29304-0491
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> [email protected]
>> http://www.ch2m.com
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Greg McGahan
>> Sent: Wednesday, February 24, 2010 7:22 PM
>> To: [email protected]
>> Subject: RE: pull stations
>>
>> This is a horse of a different color. It is a 9 story Motel with 2 levels of
>> PG underneath. The PG is approx double the footprint of the upper levels and
>> above the 2nd level of parking there is an outdoor pool deck 150' long or
>> so. There is also one stubby stairwell that goes from the 1st level  of PG
>> to the 2nd level and stops. The AHJ required a hose valve in the stubby
>> stair and one on the Pool Deck. Since both of these Valves are exposed to
>> freezing temps, the AHJ wanted a Non-Interlock PA valve to feed these 2 Hose
>> valves with a pull station adjacent to each HV. FD  pulls stations,
>> activates Solenoid at PA valve and they have water to formerly dry
>> Standpipes. Seemed like a straightforward approach to me, although a simple
>> Dry Standpipe with a Dry Valve would probably have worked just as well. I
>> can't remember why he would not allow that.
>>
>> Greg McGahan
>>
>> Living Water Fire Protection
>>  (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of
>> [email protected]
>> Sent: Wednesday, February 24, 2010 4:40 PM
>> To: [email protected]
>> Subject: RE: pull stations
>>
>> Is this pull station located at the riser next to the PA valve to comply
>> with NFPA 13,  7.3.1.2 or is it somewhere else?  How is it tied into the PA
>> system,  I seemed to miss that description.
>>
>>
>> Craig L. Prahl, CET
>> Fire Protection Specialist
>> Mechanical Department
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> PO Box 491, Spartanburg, SC  29304-0491
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> [email protected]
>> http://www.ch2m.com
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Greg McGahan
>> Sent: Wednesday, February 24, 2010 5:32 PM
>> To: [email protected]
>> Subject: RE: pull stations
>>
>> EOR just called me again, and I quote:
>>
>> "Fire alarms are life safety and supposed to go off way before the
>> sprinklers activate. Sprinklers are for property protection and not life
>> safety. This has been drilled in to me through training"
>>
>> He said the fact that the Potter website references NFPA #72 stating that
>> failure of the (releasing panel) shall not impair the operation of the
>> sprinkler system proves that.....(I don't get that either)
>>
>> Well now I know, and here I have been thinking that what I do is important.
>>
>> But the pull station/releasing device problem is solved at least.
>>
>> Greg McGahan
>>
>> Living Water Fire Protection
>>  (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Greg McGahan
>> Sent: Wednesday, February 24, 2010 1:51 PM
>> To: [email protected]
>> Subject: RE: pull stations
>>
>> No, that would be too simple.... I am the contractor and the EOR is saying
>> it in is in our scope of work, no big deal. The issue is that he didn't want
>> the "releasing devices" tied into the alarm system and wanted them installed
>> in accordance with NFPA #13.  The "RD" specified by the AHJ to be electric
>> (this is the AHJ's brainchild/requirement) and that it should electrically
>> release the solenoid on the Preaction valve. He said NFPA #72 doesn't apply
>> to the "RD's".
>>
>> I said no way. BTW, the AHJ said no way as well. He wants the "Pull
>> Stations" monitored for integrity, so if there is a bad wire, etc they get a
>> trouble signal.
>>
>> Greg McGahan
>>
>> Living Water Fire Protection
>>  (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Forest Wilson
>> Sent: Wednesday, February 24, 2010 10:32 AM
>> To: [email protected]
>> Subject: RE: pull stations
>>
>> I would suspect the problem is the EOR may be telling the sprinkler
>> contractor it is his scope of work, not the alarm contractor scope of work.
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of
>> [email protected]
>> Sent: Wednesday, February 24, 2010 11:22 AM
>> To: [email protected]
>> Subject: RE: pull stations
>>
>> Ok, so is there a problem with his definition?   By NFPA 72 definition a
>> pull station is an initiating device.  Its actuation initiates a response.
>> So in the case of the preaction system it is an initiating device since it
>> initiates opening of the PA valve.
>>
>> Whatever it's called, whether it be pull station or releasing device is
>> pretty much irrelevant.
>>
>>
>> Craig L. Prahl, CET
>> Fire Protection Specialist
>> Mechanical Department
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> PO Box 491, Spartanburg, SC  29304-0491
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> [email protected]
>> http://www.ch2m.com
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Greg McGahan
>> Sent: Wednesday, February 24, 2010 11:03 AM
>> To: [email protected]
>> Subject: pull stations
>>
>> Got an engineer telling me that a "pull station" wired to a non-interlock
>> pre-action system is NOT an alarm device and is part of the sprinkler system
>> per NFPA #13. He is calling it a releasing device and not a "pull station"
>> by definition.
>>
>> ???thoughts?
>>
>> Greg McGahan
>>
>> Living Water Fire Protection
>> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to