To my esteemed colleagues:

I have an aircraft hangar I am looking at and would like clarification on 
sprinkler / branchline spacing. I know what I think ;-)
However, I would like the combined knowledge of all of you as to the actual 
requirements of the NFPA standards.

The hangar is a 32,000 suare feet Group-I hanger with a door opening to 
accomodate a 36 ft tail height.
The chosen fire protection scheme is Option-3, a closed-head wet-pipe sprinkler 
system at .17 gpm / 15,000 square feet and a low-level hi-ex foam system.
The building is a metal-purlin building with 25 ft bay spacing.

NFPA-409 requires a maximum 130 sf sprinkler spacing with a maximum distance of 
12 feet between the sprinklers or the branch-lines.
NFPA-409 does not reference NFPA-13 for sprinkler or branch-line spacing.

Question:

In a building with 25 ft bays would one be allowed to space the branch-lines at 
12'-6" as indicated in NFPA-13 for storage bays at 25 feet spacing in lieu of 
the 12 feet as indicated in NFPA-409?

Thanks,

Ray Vance - SET
Chief Sales Designer
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com<http://www.waynefire.com>
407-877-5563   office
321-436-2184   mobile